The transmission distance of the InfiniBand cable depends on the type, rate, and quality of the cable.
According to the IBTA standard, the maximum transmission distance of InfiniBand cables is shown in the following table:
Rate |
Copper Cable |
Fiber Optic Cable |
SDR (10 Gb/s) |
15m |
300m |
DDR (20 Gb/s) |
10m |
300m |
QDR (40 Gb/s) |
7m |
300m |
FDR (56 Gb/s) |
5m |
300m |
EDR (100 Gb/s) |
3m |
100m |
HDR (200 Gb/s) |
3m |
100m |
NDR (400 Gb/s) |
2m |
100m |
It can be seen that the maximum transmission distance of copper cables decreases with the increase of the rate, while the maximum transmission distance of fiber optic cables is relatively stable.
However, these data are only theoretical limit values, and factors such as the quality of the cable, the loss of the connector, and the temperature and humidity of the environment must also be considered.
Therefore, when choosing InfiniBand cables, you need to consider the performance and cost of the cables according to the actual network needs and conditions.
People Also Ask
Related Articles

800G SR8 and 400G SR4 Optical Transceiver Modules Compatibility and Interconnection Test Report
Version Change Log Writer V0 Sample Test Cassie Test Purpose Test Objects:800G OSFP SR8/400G OSFP SR4/400G Q112 SR4. By conducting corresponding tests, the test parameters meet the relevant industry standards,

What Is the Minimum Bend Radius of an Optical Fiber?
The minimum bend radius of an optical fiber is defined as the smallest radius to which the fiber can be bent while still maintaining normal transmission of optical signals. In

AEC Active Cable Testing Solution – Deciphering AEC Performance Step by Step
With the continuous expansion of data centers and the increasing demand for high-performance computing, the AEC (Active Electrical Cable) has emerged as an effective high-speed, short-distance transmission solution. Major cloud

Why Do 400G/100G Optical Ports in Switches Require Forward Error Correction (FEC)?
Introduction Optical networks require the use of Forward Error Correction (FEC) to guarantee reliable communication. Similar to how a reader may overlook a single spelling mistake in a text but

OCP EMEA 2025: FiberMall’s 1.6T Pluggable Optical Module Based on 224G per Lane
The rapid growth of artificial intelligence (AI) and machine learning has driven a substantial demand for higher bandwidth, making the 224G per lane configuration essential. Enhanced energy efficiency is equally

OCP EMEA 2025: FiberMall Demonstrates 800G Pluggable Optical Modules with Immersion Cooling Systems
Traditional pluggable optical modules incorporate digital signal processors (DSPs) that perform full digital equalization for both electrical and optical signals. Because these DSPs are power-intensive, accounting for over 40% of

New H3C Unveils the S12500AI: A New Generation AI Network Solution Based on the DDC Architecture
Recently, New H3C introduced its groundbreaking lossless network solution and compute cluster switch—the H3C S12500AI—built upon the DDC (Diversity Dynamic-Connectivity) architecture. Tailored to meet the demanding requirements of scenarios involving
Related posts:
- Is the CX7 NDR 200 QSFP112 Compatible with HDR/EDR Cables?
- If the Server’s Module is OSFP and the Switch’s is QSFP112, can it be Linked by Cables to Connect Data?
- Is UFM as Functional as Managed Switch and Unmanaged Switch?
- Can the CX7 NIC with Ethernet mode interconnect with other 400G Ethernet switches that support RDMA?